Determine the minimum ampacity of conductors serving a continuous duty, Design B, 3-phase, 208-volt, 10 hp, induction-type motor.

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

Determine the minimum ampacity of conductors serving a continuous duty, Design B, 3-phase, 208-volt, 10 hp, induction-type motor.

Explanation:
Sizing motor conductors for continuous-duty uses a multiplier of 1.25 on the motor’s full-load current. For a 10 hp, three-phase motor at 208 V, the full-load current from NEC motor tables is 30.8 A. Applying 125% gives 30.8 × 1.25 = 38.5 A. So the minimum ampacity the conductors must have is 38.5 A. The other numbers would come from using a different full-load current or omitting the 125% factor.

Sizing motor conductors for continuous-duty uses a multiplier of 1.25 on the motor’s full-load current. For a 10 hp, three-phase motor at 208 V, the full-load current from NEC motor tables is 30.8 A. Applying 125% gives 30.8 × 1.25 = 38.5 A. So the minimum ampacity the conductors must have is 38.5 A. The other numbers would come from using a different full-load current or omitting the 125% factor.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy