For a 200-A service with a transformer feeding a single set of 3/0 AWG feeders, the largest copper GEC size to the water line is ___ AWG.

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

For a 200-A service with a transformer feeding a single set of 3/0 AWG feeders, the largest copper GEC size to the water line is ___ AWG.

Explanation:
Grounding electrode conductor size to a water pipe is set by NEC 250.66 and is based on the rating of the service equipment (or the overcurrent device protecting it). For a 200-A service, the minimum copper GEC size to the water line is two AWG. The presence of a transformer feeding a single set of 3/0 feeders does not change this requirement—the electrode conductor sizing is tied to the service rating, not the feeder size. Smaller than the minimum would not satisfy the code; larger sizes are permissible but typically the minimum that meets the requirement is the standard answer.

Grounding electrode conductor size to a water pipe is set by NEC 250.66 and is based on the rating of the service equipment (or the overcurrent device protecting it). For a 200-A service, the minimum copper GEC size to the water line is two AWG. The presence of a transformer feeding a single set of 3/0 feeders does not change this requirement—the electrode conductor sizing is tied to the service rating, not the feeder size. Smaller than the minimum would not satisfy the code; larger sizes are permissible but typically the minimum that meets the requirement is the standard answer.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy