For Motor #1, the smallest circuit conductors between the wireway and the safety switch (75°C terminations) are which AWG?

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

For Motor #1, the smallest circuit conductors between the wireway and the safety switch (75°C terminations) are which AWG?

Explanation:
When sizing conductors for a motor, you must use enough ampacity to carry the motor’s full-load current, and you can use the 75°C ampacity column if the termination devices are rated 75°C. So you look up the motor’s full-load current on its nameplate and then pick the smallest conductor size whose 75°C ampacity is at least that current. For this motor, 12 AWG at 75°C is typically about 25 A, which isn’t enough if the motor’s full-load current is higher than 25 A. Moving up to 10 AWG provides about 30 A of ampacity in the 75°C column, which meets or exceeds the motor’s full-load current. Although 8 AWG would also satisfy the requirement, the goal is the smallest size that meets the rating, so 10 AWG is the correct choice.

When sizing conductors for a motor, you must use enough ampacity to carry the motor’s full-load current, and you can use the 75°C ampacity column if the termination devices are rated 75°C. So you look up the motor’s full-load current on its nameplate and then pick the smallest conductor size whose 75°C ampacity is at least that current.

For this motor, 12 AWG at 75°C is typically about 25 A, which isn’t enough if the motor’s full-load current is higher than 25 A. Moving up to 10 AWG provides about 30 A of ampacity in the 75°C column, which meets or exceeds the motor’s full-load current. Although 8 AWG would also satisfy the requirement, the goal is the smallest size that meets the rating, so 10 AWG is the correct choice.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy