In a 3-gang masonry box stamped at 47.4 in3 that will contain two 4-way switches and one 3-way switch, with eleven 12 AWG THHN/THWN conductors terminating on the switches and no EGCs installed, how many additional 12 AWG conductors may be pulled through this box unspliced and unlooped?

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

In a 3-gang masonry box stamped at 47.4 in3 that will contain two 4-way switches and one 3-way switch, with eleven 12 AWG THHN/THWN conductors terminating on the switches and no EGCs installed, how many additional 12 AWG conductors may be pulled through this box unspliced and unlooped?

Explanation:
Box fill is determined by NEC 314.16(B): every conductor that originates outside the box and terminates or is spliced inside counts as one fill unit, every conductor that passes through unspliced counts as a half unit, all equipment grounding conductors (EGCs) together count as one unit, and each device yoke adds one unit. For 12 AWG conductors, one fill unit equals 2.25 in³. In this 3-gang masonry box, eleven 12 AWG conductors terminate on the switches, so they contribute 11 units. The box has three devices (two 4-ways and one 3-way), so add 3 more units for the device yokes. Total fill units so far: 11 + 3 = 14. Volume used by these 14 units: 14 × 2.25 = 31.5 in³. Box volume is 47.4 in³, so remaining volume is 47.4 − 31.5 = 15.9 in³. Through conductors count as one-half of a unit each, which is 1.125 in³ per 12 AWG conductor. Maximum additional through conductors = floor(15.9 ÷ 1.125) = floor(14.13) = 14. Therefore, up to 14 more 12 AWG conductors could be pulled through unspliced and unlooped in this box.

Box fill is determined by NEC 314.16(B): every conductor that originates outside the box and terminates or is spliced inside counts as one fill unit, every conductor that passes through unspliced counts as a half unit, all equipment grounding conductors (EGCs) together count as one unit, and each device yoke adds one unit. For 12 AWG conductors, one fill unit equals 2.25 in³.

In this 3-gang masonry box, eleven 12 AWG conductors terminate on the switches, so they contribute 11 units. The box has three devices (two 4-ways and one 3-way), so add 3 more units for the device yokes. Total fill units so far: 11 + 3 = 14. Volume used by these 14 units: 14 × 2.25 = 31.5 in³. Box volume is 47.4 in³, so remaining volume is 47.4 − 31.5 = 15.9 in³.

Through conductors count as one-half of a unit each, which is 1.125 in³ per 12 AWG conductor. Maximum additional through conductors = floor(15.9 ÷ 1.125) = floor(14.13) = 14. Therefore, up to 14 more 12 AWG conductors could be pulled through unspliced and unlooped in this box.