In a dual-conduit installation for a 3-phase system, with three 350 kcmil conductors in each parallel run and a 600-A circuit breaker, what is the smallest EGC gauge allowed to be installed in each conduit?

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

In a dual-conduit installation for a 3-phase system, with three 350 kcmil conductors in each parallel run and a 600-A circuit breaker, what is the smallest EGC gauge allowed to be installed in each conduit?

Explanation:
The rule being tested is how to size the equipment grounding conductor (EGC) based on the overcurrent protection device. For an overcurrent device rating of 600 A, NEC 250.122 requires a copper EGC of 1 AWG (or an aluminum EGC of 1/0 AWG). This sizing is tied to the protective device, not to the size of the current-carrying conductors, so even with three 350 kcmil conductors in each parallel run and two parallel conduits, the minimum EGC in each conduit must meet that 1 AWG copper requirement. In a dual-conduit setup, you still provide a ground path in each conduit with at least this size so a ground-fault current can return quickly enough to trip the 600 A breaker. Therefore, the smallest allowed EGC gauge in each conduit is 1 AWG copper. The other options are larger than the minimum and thus not the smallest permissible gauge.

The rule being tested is how to size the equipment grounding conductor (EGC) based on the overcurrent protection device. For an overcurrent device rating of 600 A, NEC 250.122 requires a copper EGC of 1 AWG (or an aluminum EGC of 1/0 AWG). This sizing is tied to the protective device, not to the size of the current-carrying conductors, so even with three 350 kcmil conductors in each parallel run and two parallel conduits, the minimum EGC in each conduit must meet that 1 AWG copper requirement. In a dual-conduit setup, you still provide a ground path in each conduit with at least this size so a ground-fault current can return quickly enough to trip the 600 A breaker. Therefore, the smallest allowed EGC gauge in each conduit is 1 AWG copper. The other options are larger than the minimum and thus not the smallest permissible gauge.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy