In a tapped feeder scenario with a 4160 to 2400 V three-phase transformer 225 kVA in nonsupervised location, Z = 4%. The transformer supplies a 3Ø fused safety switch. The fuses can have rating not more than ___ amps.

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

In a tapped feeder scenario with a 4160 to 2400 V three-phase transformer 225 kVA in nonsupervised location, Z = 4%. The transformer supplies a 3Ø fused safety switch. The fuses can have rating not more than ___ amps.