The smallest THHN/THWN copper grounded conductor that can be installed for a service is ___ when the ungrounded conductors are 1/0 THWN/THHN copper.

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

The smallest THHN/THWN copper grounded conductor that can be installed for a service is ___ when the ungrounded conductors are 1/0 THWN/THHN copper.

Explanation:
Sizing the grounded conductor (the neutral) in a service is driven by the service’s overcurrent protection. When the ungrounded conductors are 1/0 copper, you’re dealing with a fairly large service, typically around 150 A. For that level of protection, the neutral must be at least a certain minimum size, which in this scenario is 6 AWG copper. So the smallest grounded conductor you can install for this service is 6 AWG. The other options listed (2, 3, or 1/0) are larger conductors and would be acceptable, but they aren’t the smallest size that meets the requirement.

Sizing the grounded conductor (the neutral) in a service is driven by the service’s overcurrent protection. When the ungrounded conductors are 1/0 copper, you’re dealing with a fairly large service, typically around 150 A. For that level of protection, the neutral must be at least a certain minimum size, which in this scenario is 6 AWG copper. So the smallest grounded conductor you can install for this service is 6 AWG. The other options listed (2, 3, or 1/0) are larger conductors and would be acceptable, but they aren’t the smallest size that meets the requirement.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy