The smallest THHN/THWN copper grounded conductor for a service is ___ when the ungrounded conductors are 1/0 THWN/THHN copper and the load on the neutral is expected to be 120 amps.

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

The smallest THHN/THWN copper grounded conductor for a service is ___ when the ungrounded conductors are 1/0 THWN/THHN copper and the load on the neutral is expected to be 120 amps.

Explanation:
The key idea is sizing the neutral (grounded conductor) to carry the actual neutral current. For THHN/THWN copper, you use the ampacity from NEC Table 310.16 (75°C column). At 75°C, the ampacities are approximately: - 3 AWG ≈ 100 A - 2 AWG ≈ 115 A - 1 AWG ≈ 130 A - 1/0 AWG ≈ 150 A Since the neutral is expected to carry 120 A, the smallest conductor that can safely carry that load is 1 AWG. A 2 AWG (115 A) isn’t enough, and a 3 AWG (100 A) isn’t enough either. The 1 AWG size meets and exceeds the required 120 A, while smaller sizes do not.

The key idea is sizing the neutral (grounded conductor) to carry the actual neutral current. For THHN/THWN copper, you use the ampacity from NEC Table 310.16 (75°C column). At 75°C, the ampacities are approximately:

  • 3 AWG ≈ 100 A
  • 2 AWG ≈ 115 A

  • 1 AWG ≈ 130 A

  • 1/0 AWG ≈ 150 A

Since the neutral is expected to carry 120 A, the smallest conductor that can safely carry that load is 1 AWG. A 2 AWG (115 A) isn’t enough, and a 3 AWG (100 A) isn’t enough either. The 1 AWG size meets and exceeds the required 120 A, while smaller sizes do not.